Please read Rules for forum posts before reporting your issue or asking a question. OPC Labs team is actively monitoring the forums, and replies as soon as possible. Various technical information can also be found in our Knowledge Base. For your convenience, we have also assembled a Frequently Asked Questions page.
Do not use the Contact page for technical issues.
- Forum
- Discussions
- QuickOPC-Classic in .NET
- Reading, Writing, Subscriptions, Property Access
- Timeouts with OPC write, using Simatic OPC server remotely
Timeouts with OPC write, using Simatic OPC server remotely
Please Log in or Create an account to join the conversation.
- Peter Siegel
- Visitor
With the analyzer tool we were able to trace the gabs in the communication back to the Simatic.net OPC Server. During Times of heavy IO Loads on the System, the Communication between S7 PLC and Simatic.net Server is paused/halted. As a consequence of this, no events are relayed via opc to the clients.
Again thank you for your help.
Peter
Please Log in or Create an account to join the conversation.
Great - please download and install the <a href="/LinkClick.aspx?fileticket=W7HYzaSQoWk%3d&tabid=195">OPC Analyzer tool.
After installing, enter any necessary information in the "Category Filter" and "Remote Machine Name" fields, and press the "Refresh" button. Then, select your target OPC server from the "Server" drop-down, and make sure the trace is started (if "TRACE STOPPED" is displayed, press the "start trace" button).
You then need to modify your application to connect to the OPC Analyzer instead of your real target OPC server; the OPC Analyzer acts as an intermediate logger. The ProgID of the OPC Analyzer is "OpcTestLab.OpcAnalyzer.1". You can then run your application, and you should see the trace being collected in the OPC analyzer. Make handnotes of times of any relevant events, such as the time when you have started the application, and when the exception occurred. After you are finished, select File -> Save Trace in the Opc Analyzer, save the .TRA file, and send it to us - ideally, attach it to your reply in this forum.
Note: The OPC Analyzer tool is available to OPC corporate members only, thus the download is only permitted to your user account (you must be logged into our site), and you can only use it for the purpose of troubleshooting this particular problem.
Please Log in or Create an account to join the conversation.
- Peter Siegel
- Visitor
You can contact me at PeterS(at)4ahead.com
thanks Peter
Please Log in or Create an account to join the conversation.
Would you be willing to install OPC Analyzer tool according to our instructions, and collect the information necessary to diagnose the problem? The analyzer acts as intermediary between the OPC Client and Server, and logs the OPC methods calls and callbacks.
Please Log in or Create an account to join the conversation.
- Peter Siegel
- Visitor
I'm writing, and sometimes get a Timeout ( but the value was set ). While executing write statements incoming subscription events seemed to be blocked too. Is there a way to avoid this behavoir?
I'm using:
easyDAClient = new EasyDAClient();
easyDAClient.ClientMode.AllowAsynchronousMethod = false;
easyDAClient.ClientMode.AllowSynchronousMethod = true;
easyDAClient.ClientMode.DesiredMethod = DAReadWriteMethod.Synchronous;
easyDAClient.Timeouts.ReadItem = 50000;
easyDAClient.Timeouts.WriteItem = 50000;
easyDAClient.Timeouts.GetProperty = 36000;
easyDAClient.UpdateRates.ReadAutomatic = 250;
easyDAClient.HoldPeriods.TopicRead = 24 * 60 * 60 * 1000;
easyDAClient.HoldPeriods.TopicWrite = 24 * 60 * 60 * 1000;
thanks
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.
first, I can confirm that there is no problem with the code itself (except that I cannot verify the validity of the ItemID you have used).
Second, using this line instead:
list.Add(new DAItemValueArguments("", "OPCLabs.KitServer.2", "Simulation.Register_I4", val++));
with our simulation servers works fine, gives no timeout. This means that the servers behave differently.
Before we go into some difficult troubleshooting (e.g. using the Opc Analyzer), I suggest that you try to force the component to use just Synchronous Writes. To do so, add this line (after instantiating the component):
_OpcClient.ClientMode.AllowAsynchronousMethod = false;
Best regards,
Zbynek Zahradnik, OPC Labs
Please Log in or Create an account to join the conversation.
<span style="font-family: "Tahoma","sans-serif"; font-size: 10pt; mso-fareast-font-family: 'Times New Roman'">From:<span style="font-family: "Tahoma","sans-serif"; font-size: 10pt; mso-fareast-font-family: 'Times New Roman'"> M.
Sent: Tuesday, June 14, 2011 3:49 PM
To: Zbynek Zahradnik
Subject: ...
<span style="font-family: "Tahoma","sans-serif"; font-size: 10pt; mso-fareast-font-family: 'Times New Roman'">
Hello Mr. Zahradnik!
In the attachment you will find the project we discussed.
Server:
SIMATIC NET 2006, V6.4
OPC.SimaticNET
(on a different machine as the development system)
Thank you in advance for your support.
Any way to write down to the OPC-Server will help us at the moment (if reading with QuickOPC still works J)
Kind regards
M.