Professional OPC
Development Tools

logos

Online Forums

Technical support is provided through Support Forums below. Anybody can view them; you need to Register/Login to our site (see links in upper right corner) in order to Post questions. You do not have to be a licensed user of our product.

Please read Rules for forum posts before reporting your issue or asking a question. OPC Labs team is actively monitoring the forums, and replies as soon as possible. Various technical information can also be found in our Knowledge Base. For your convenience, we have also assembled a Frequently Asked Questions page.

Do not use the Contact page for technical issues.

Maximum number of nodes in multiple read/write functions

More
22 Dec 2016 10:28 #4686 by RH
Thank you for that quick response!

Please Log in or Create an account to join the conversation.

More
22 Dec 2016 10:18 #4685 by support
This error comes from the server. The client does not know what the server limit is.

Either the server needs to be reconfigured, or you need to change your client code to work with fewer variables at a time.

Please Log in or Create an account to join the conversation.

More
22 Dec 2016 09:56 #4683 by RH
Hello,

I use the multiple read function on an OPC UA server to read variables. For about 20 variables, this is no problem at all. But now, I want to read around 190 variables at once, using the multiple read function, but I always get an exception saying "BadTooManyOperations". Do I need to set a parameter to get this fixed?

Best regards

Please Log in or Create an account to join the conversation.

Moderators: support
Time to create page: 0.044 seconds