Please read Rules for forum posts before reporting your issue or asking a question. OPC Labs team is actively monitoring the forums, and replies as soon as possible. Various technical information can also be found in our Knowledge Base. For your convenience, we have also assembled a Frequently Asked Questions page.
Do not use the Contact page for technical issues.
Can't even connect!
Regards,
Martin
Please Log in or Create an account to join the conversation.
The NodeID you have specified does not contain namespace URI or namespace index, and it is therefore assumed to be in reserved namespace with index 0 and URI opcfoundation.org/UA/ .
But according to the UAExpert screenshot, the node you actually have in mind lives in namespace index 4. The namespaces are important part of the NodeID and nothing works without them in OPC UA.
You should therefore specify the node e.g. like this:
ns=4;s=25_SPS->CC.behaelter_b.level.level_act
Even better, you should actually use a namespace URI ("nsu=..."), and not a namespace index ("ns=..."), because the namespace index may change between sessions if the server decides to do so.
Some related reading:
- opclabs.doc-that.com/files/onlinedocs/QuickOpc/Latest/User%2.../webframe.html#Node%20IDs.html
- opclabs.doc-that.com/files/onlinedocs/QuickOpc/Latest/User%2...indices%20in%20Node%20Ids.html
Best regards
Please Log in or Create an account to join the conversation.
The Delphi code is the following:
procedure TForm1.FormCreate(Sender: TObject);
var EasyUAClient : TEasyUAClient;
begin
EasyUAClient := TEasyUAClient.create(NIL);
try
Edit1.Text := EasyUAClient.ReadValue('opc.tcp://konti_breit:4870',
'25_SPS->CC.behaelter_b.level.level_act');
except
on e:exception do begin
MessageDlg(e.message, mtError, [mbOK], 0);
end;
end;
end;
Martin
Please Log in or Create an account to join the conversation.
Please post the code here. And, post an image (or images) of UAExpert showing that it can read the same attribute of the same node (the NodeID should be visible).
The default attribute is Value.
Best regards
Please Log in or Create an account to join the conversation.
Now i get the error "Status is not good: BadAttributeInvalid" (again the same code as above).
UAExpert still connects clean and shows me all values.
I'm in need of a working solution.
Please Log in or Create an account to join the conversation.
I've downloaded and installed the new build according to yout kind posting.
I tried the same code, but now i get another exception:
"Cannot lock the OPC-UA client session because it is not connected"
I used the same code as above. Is there anything i have to change in the code to get the workaround running?
Regards,
Martin
Please Log in or Create an account to join the conversation.
Given that this is a second occurrence of the issue (albeit probably with the same OPC UA server), we have decided to try to put a workaround into the client component. The problem with it is that we can only work with the information we have from you, and cannot verify some communication details, and cannot test that the workaround actually resolves the problem.
We have made a new build of version 2016.2 with the workaround. Please download the current build from this Web site (it is build 512.1 or later - check it on the installer first page; the previous one was 502.1), reinstall it, rebuild your project, and retest.
We still believe it is a server issue, but it is our interest to be able to work well with as many servers as possible.
Regards
Please Log in or Create an account to join the conversation.
support wrote: If you could provide us with a demo version of the server (if PC based), or open access to it over the Web, or provide us with a virtual machine image with the server in it (if PC based), we might be able to investigate the details and possibly even to include a workaround on our side.
I'm afraid i can't do that. I even can't change the OPC server settings. This is not in my hands. The panels, opc servers and nc's are under control of another department/company. I've contacted them to change the server settings as described in the other thread. But it would make me happy if there was any possibility to use a client side workaround for this problem.
Regards,
Martin
Please Log in or Create an account to join the conversation.
When i connect to it via UaExpert, it reports the following:
"Siemens OPC UA Server for WinCC Panel RT"
btw, i own a commerial license of your QuickOPC product.
I will study the mentioned thread and give it a try.
Regards, Martin
Please Log in or Create an account to join the conversation.
In our view the cause was a server not compliant to the OPC UA specs. The details are described in the earlier thread so they do not have to be repeated here.
The "workaround" was to configure the server to provide unsecured endpoints only. It should also be possible to define the UAEndpointDescriptor on the client side to allow only unsecured endpoints - the code for that is also in that earlier thread, though the customer reported that it had not helped.
If you could provide us with a demo version of the server (if PC based), or open access to it over the Web, or provide us with a virtual machine image with the server in it (if PC based), we might be able to investigate the details and possibly even to include a workaround on our side.
BTW, which OPC UA server are you connecting to?